I was wondering with all this heat, my shop isn't cooled with AC, if that waterhose in the back of the M42 should ever be leaking water from the AC unit? It has been bone dry for as long as I can remember. Is there a way to get inside to check for a possible clog? Up near Toronto - crazy hot last few days expecially with a high humidity.
It is just an overflow for the condensate tray. The cover for the control cabinet cooler on our machine is just secured with 10-12 screws around the edge. I've had to remove it before on our CS43 to service the squirrel-cage fan. Ours seized, and I've had to replace it due to dust ingress. It's possible that it is clogged, would be quick to check.
_____________
Win 10 Pro 64 bit on MSI Z390M Pro4
Intel core i7 9700KF 3.6GHz (OC 4.2Ghz)
32 gig RAM, NVIDIA GeForce GTX 1050 Ti
NVME SSM2HD 1TB NTFS
As Stuart mentioned, its just when there is condensation on the evaporator core for the A/C unit. If there is whole bunch of humidity you might see it spit a bit of water. But its only conditioning the air within the control cabinet. So as long as the cabinet is mostly sealed as it should be, the A/C unit pulls air from within the cabinet, cools it, then pushes it back in the cabinet. It shouldn't be exchanging much if any shop air. So even if it is humid outside, the air in the cabinet is likely not humid.
Thanks - agreed. Will open it up regardless, seems to work fine for a few hours then the cooling STOPS... so my guess is there is a clog somewhere once the pan gets filled.
I just, set a bucket under it, this time of year.
And I make sure the air filter, is seated properly in the channel.
that is how the dust gets in.
So you mite, have to give it a good, cleaning, asap